Understanding the minimum ampere rating for a fused switch on a 25 hp, 480-volt AC motor is crucial for electricians. Learn how to properly calculate and select fuse sizes to ensure compliance and safety.

When you're gearing up for the Journeyman Electrician Practice Exam, one crucial topic to wrap your head around is selecting the right ampere rating for a general-use fused switch. It might sound technical, but stick with me; it’s simpler than you think! Imagine being at a service call, tasked with ensuring that a 25 hp, 480-volt three-phase AC motor is hooked up safely—that’s where understanding these ratings comes in handy.

So, let’s break it down, shall we? You’re faced with a motor that has a Full Load Amperage (FLA) of 32 amperes. The pressing question is: what’s the minimum ampere rating for the fused switch? It’s a bit like shopping for the right pair of shoes. You need something that fits well, is comfortable, and gets the job done!

To find our answer, we turn to the National Electrical Code (NEC) guidelines. NEC has laid out the rules for motor applications, saying your minimum fuse or breaker size should be at least 125% of the Full Load Amperage. Sounds simple, right? Let me explain how we calculate that.

First, you take your FLA of 32 amperes and multiply it by 1.25. So, 32 A x 1.25 gives us 40 amperes. But wait! It doesn’t stop there. The NEC does not deal with fractions when it comes to actual fuse ratings; you need to select an available size. What’s the next standard size greater than 40 amps? Drumroll, please... it’s 45 amperes!

Now here’s a little twist—if you were to consider the option of 39 amperes, you’d be making a mistake. This size falls short of the minimum needed to protect the motor against potential overloads. You need to think of it this way: would you wear shoes that are just a tad too small? Nope! The consequences could be painful. Just like motors, they need enough support.

By sticking with the 45-ampere option, you’re ensuring that the motor has the right protection while still allowing for those little surges that happen when the motor starts up. Remember, a motor can draw more current during that initial period. So, choosing the correct size isn't just checking a box—it’s about safety and performance.

You know something interesting? Each time you select the right fuse or breaker, you’re not just complying with NEC standards; you're also stepping up as a professional who puts safety first. That's something to be proud of! And perhaps even more enlightening, the right knowledge today could save a costly mishap tomorrow!

In wrapping up, following the NEC guidelines isn’t just about passing an exam; it's about ensuring your work is up to code, keeping equipment running smoothly, and—the cherry on top—having peace of mind.

So next time you're faced with determining the minimum ampere rating for any motor, remember: always take 125% of the FLA, round up to the nearest standard size, and keep your motor operating safe and sound!